080425-1424 EST
I started construction of my home in 1965 and completed and occupied it in Oct of 66. All switching is done with GE RR-5 or 6 relays. These plug into busbars in gang boxes. There are a total of about 50 to 60 relays. There are no motor loads and probably not over 500 W on any switch. A number of these switch 8 ft Slimline fixtures. The RR-6 relays have auxiliary contacts for pilot light operation. I have a box labeled 1983 that contains failed relays. There are about 8 relays in the box and all are RR-6. These are not all the relays that have failed, but most of them. The relays have failed over the years probably starting in 1983, 17 years from initial installation would be the starting time. Not all failures were related to high useage, and not all are RR-6.
I have never had a failure due to coil burn out. All failures are the result of loss of bi-state ability. Many of these exhibit temperature sensitivity, and thus work sometimes. I believe all failures are to the off state, failure to stay turned on when triggered to on.
I have conjectured that the mechanical stress created from the busbars may have been part of the problem.
Bi-stable relays are a great way to design a control system, and why I chose to use them. I do not consider conventional switching a satisfactory system.
The RR-5 and 6 use a spring contact for termination of the load wiring. This has never proved to be a problem. However, I do not consider it a high reliability connection.
What have you experienced in the reliability of these relays or competitors?
.
I started construction of my home in 1965 and completed and occupied it in Oct of 66. All switching is done with GE RR-5 or 6 relays. These plug into busbars in gang boxes. There are a total of about 50 to 60 relays. There are no motor loads and probably not over 500 W on any switch. A number of these switch 8 ft Slimline fixtures. The RR-6 relays have auxiliary contacts for pilot light operation. I have a box labeled 1983 that contains failed relays. There are about 8 relays in the box and all are RR-6. These are not all the relays that have failed, but most of them. The relays have failed over the years probably starting in 1983, 17 years from initial installation would be the starting time. Not all failures were related to high useage, and not all are RR-6.
I have never had a failure due to coil burn out. All failures are the result of loss of bi-state ability. Many of these exhibit temperature sensitivity, and thus work sometimes. I believe all failures are to the off state, failure to stay turned on when triggered to on.
I have conjectured that the mechanical stress created from the busbars may have been part of the problem.
Bi-stable relays are a great way to design a control system, and why I chose to use them. I do not consider conventional switching a satisfactory system.
The RR-5 and 6 use a spring contact for termination of the load wiring. This has never proved to be a problem. However, I do not consider it a high reliability connection.
What have you experienced in the reliability of these relays or competitors?
.