macmikeman
Senior Member
- Location
- Planet macmikeman
Yesterday I got called to redo a grounding electrode conductor connection by the local inspector checking my most recent house wiring job. I had run my gec to my gr rod and then non spliced over to a water pipe spigot nearby that comes up out of the ground after running below the slab over to its connection point to the rest of the cold water pipes. The inspector wants my gec connection to the water supply made at the water service for the house where the pressure reducer is located. He told me it needed to be within 5 ft of the entry to the building. My reply is that code is refering to INTERIOR metal water piping as per 250.52 (a) (1) and that any exterior underground metal water pipe longer than 10 feet is ok. He wasn't budging. Anybody got an opinion on this?