My understanding is - that apart from lightning - which some areas have little or none of, not everywhere is Florida - is to bring conductive surfaces of electrical apparatus 'closer' to the same potential.
That may have been the intent but as the grapic shows that is really not what happens.
Having a grounded conductor would be difficult without ground... (Earth) Otherwise it would be a floating neutral... And since we have a MBJ at the service, the EGC would also be floating (potential wise) and could be a shock hazard due to the difference between it and the ground (earth) you're standing on.
True, but the fact remains with a big enough 'push' the EGC and the neutral can be at a fatal potential to earth only a short distance from the electrode.
Connecting to earth is a lot like connecting to a large resister and at any distance from the connection you will have a difference of potential. (Of course an EGC is also a resister, but not nearly as much as the connection to dirt.)