Dzboyce
Senior Member
- Location
- Royal City, WA
- Occupation
- Washington 03 Electrician & plumber
Joe.
I'm in eastern Eashington. So I deal with Labor & Industries electrical inspectors also. I ushally deal with pump houses ascauxiliary structures. A plain or even thickened edge concrete slab only requires two ground rods or plates. My inspectors are fine with me just laying the ground rods in the trench, just have to have six feet between the end of one before the next one. However if the pump house has footings, I'm required to bond to the rebar (ufer). Had one that they didn't provide me with a piece of rebar stickingnoutbof the footings to bond to. The inspector gave me two options, chip out cement to find a piece of rebar to bond to, or dig a trench all the way around the building and install a ground ring. He would not accept the two ground rods I had already driven.If a building has a concrete slab but no footing it will either need rods or plates, correct? I need at least 100 characters so i'm still typing.