This is a rather elongated problem.
Synopsis: We are installing a new classroom at an existing school.
The feed for this new"service" is not the "main" service.
The specs are treating this like a new service entrance, to include bonding the neutral (which we know is incorrect).
The first service, in the new building, is a 277/480v. with the main overcurrent protection set to 300a.
Their spec shows we can use a #4 GEC in the footing. Which to me would be in line with the NEC.
That Service then feeds a transformer with a 600a. secondary. We used a #1/0
for the grounding.
That transformer then feeds a 600a. 120/208 Service. Which we used another #4 bare in the concrete envelope as the ground.
Question:
1) Was the #4 bare acceptable in both services?
2) Was the #1/0 of adequate size to ground the transformer?
The spec drawing showed the gec ufer to be a #4. Below the drawing was a grounding conductor chart which was rated by amps. It specified 400-600a.
to be a #1/0.
Synopsis: We are installing a new classroom at an existing school.
The feed for this new"service" is not the "main" service.
The specs are treating this like a new service entrance, to include bonding the neutral (which we know is incorrect).
The first service, in the new building, is a 277/480v. with the main overcurrent protection set to 300a.
Their spec shows we can use a #4 GEC in the footing. Which to me would be in line with the NEC.
That Service then feeds a transformer with a 600a. secondary. We used a #1/0
for the grounding.
That transformer then feeds a 600a. 120/208 Service. Which we used another #4 bare in the concrete envelope as the ground.
Question:
1) Was the #4 bare acceptable in both services?
2) Was the #1/0 of adequate size to ground the transformer?
The spec drawing showed the gec ufer to be a #4. Below the drawing was a grounding conductor chart which was rated by amps. It specified 400-600a.
to be a #1/0.