My AHJ requires a disconnect mounted on the exterior of the detached shed prior to the interior sub panel . This is a 60A disconnect feeding the 60A shed sub panel. I have installed two ground rods 8 feet apart.
250.32(B)(1) seems to indicate both the service disconnect and the sub panel should be connected the the GEC. My question is do I run the GEC from the GES to the sub panel and the disconnect? My AHJ sometimes wings it and not in a good way, so was hoping to get some feedback
250.32(B)(1) seems to indicate both the service disconnect and the sub panel should be connected the the GEC. My question is do I run the GEC from the GES to the sub panel and the disconnect? My AHJ sometimes wings it and not in a good way, so was hoping to get some feedback