250.64 (E), Heres what I saw at our job. A GEC coming out of a xfmr in FMC and changing over to PVC the rest of the way to the building steel termination. Wouldnt you at least bond the FMC to the xfmr case with a bonding bushing?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
250.64 (E), Wouldnt you at least bond the FMC to the xfmr case with a bonding bushing?

I wouldn't, the locknut would be fine, the problem is the other end (connected to the PVC) of the FMC is not bonded as required.

Roger
 

joeyww12000

Senior Member
Location
Chatsworth GA
What exactly would you do there? You have a 10' stick of 3/4" PVC with a male adapter to a rigid coupling, FMC male connector and about a 16" piece of FMC going to Xfmr...
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
What exactly would you do there? You have a 10' stick of 3/4" PVC with a male adapter to a rigid coupling, FMC male connector and about a 16" piece of FMC going to Xfmr...

Change the FMC to a piece of LFNC and a PVC female adapter for the transition.

Or, if the last 16" is not subject to physical damage, do away with the flex altogether and let the conductor enter the transformer exposed.