Re: GEC Functions/Misfunctions
I think that we will still need a local grounding electrode with the 4 wire service for protection from lightning and accidental contact with higher voltage systems. Also the 4 wire installation does not solve the problems caused by an open service neutral, the only advantage fo the 4 wires is to eliminate parallel paths for neutral current between the building and the utility transformer. Would the advantages of the 4 wire system jsutify the cost increase of installing that system?
Don
I think that we will still need a local grounding electrode with the 4 wire service for protection from lightning and accidental contact with higher voltage systems. Also the 4 wire installation does not solve the problems caused by an open service neutral, the only advantage fo the 4 wires is to eliminate parallel paths for neutral current between the building and the utility transformer. Would the advantages of the 4 wire system jsutify the cost increase of installing that system?