pvgreeze
Member
- Location
- Philadelphia
- Occupation
- Electrical Engineer
Hi everyone, I've been looking through threads for a discussion on this topic, and I cannot find anything specific to the issue I'm facing. The AHJ in question uses the 2017 NEC, so all references will be to that, though I think the language of the code is consistent in later versions...
I have a PV Disconnect outside of a building, line side interconnection, that is a separate service disconnect [230.2(A)(5)]. In this disconnect, I am bonding the ground (grounding) and the neutral (grounded) with a main bonding jumper sized off Table 250.102(C)(1) [250.24(B) & 250.28]. Now, I need to connect the ground in PV Disconnect to the building grounding electrode system [250.58 and 690.47(A)]. This connection will be achieved with a grounding electrode conductor (GEC), which is sized off of Table 250.66 for this building, which now has multiple [service] disconnecting means in separate enclosures [250.64(D)(2)].
My grounding electrode conductor is sized off of NEC 250.66. For this PV system, the OCPD is a 1000A fuse, with three parallel sets of service entrance conductors off the line side of the existing main circuit breaker, in parallel ferrous raceways.
Here is where I am confused. Table 250.66 requires me to only have a single 3/0 Cu GEC. A conventional service would have this GEC connected between the grounding busbar in the main switchboard and the building grounding electrode system (GES) - building steel, pipes, ground rods, etc. However, my PV Disconnect is outside of the building, and I need to tie this PV Disconnect GES to the building GES, as outlined above, with a single 3/0 Cu GEC. The easiest method to do this would be to run this GEC with the parallel ungrounded conductors & neutrals to the existing main circuit breaker and connect within the existing switchboard.
My questions are:
Would love to know thoughts and comments. I've read through several related threads, and didn't see anything that addressed this specific concern. I'll link below for reference:
I have a PV Disconnect outside of a building, line side interconnection, that is a separate service disconnect [230.2(A)(5)]. In this disconnect, I am bonding the ground (grounding) and the neutral (grounded) with a main bonding jumper sized off Table 250.102(C)(1) [250.24(B) & 250.28]. Now, I need to connect the ground in PV Disconnect to the building grounding electrode system [250.58 and 690.47(A)]. This connection will be achieved with a grounding electrode conductor (GEC), which is sized off of Table 250.66 for this building, which now has multiple [service] disconnecting means in separate enclosures [250.64(D)(2)].
My grounding electrode conductor is sized off of NEC 250.66. For this PV system, the OCPD is a 1000A fuse, with three parallel sets of service entrance conductors off the line side of the existing main circuit breaker, in parallel ferrous raceways.
Here is where I am confused. Table 250.66 requires me to only have a single 3/0 Cu GEC. A conventional service would have this GEC connected between the grounding busbar in the main switchboard and the building grounding electrode system (GES) - building steel, pipes, ground rods, etc. However, my PV Disconnect is outside of the building, and I need to tie this PV Disconnect GES to the building GES, as outlined above, with a single 3/0 Cu GEC. The easiest method to do this would be to run this GEC with the parallel ungrounded conductors & neutrals to the existing main circuit breaker and connect within the existing switchboard.
My questions are:
- Can I run a single GEC in the same raceway as phase and neutral (grounded) conductors to the point of inteconnection/the most practical tie in point to connect to the existing GES
- Can I run a single GEC in one raceway when there are multiple parallel raceways, several of which would not contain GECs
Would love to know thoughts and comments. I've read through several related threads, and didn't see anything that addressed this specific concern. I'll link below for reference:
GEC for PV Disconnects
For a supply side connection, do I really need a GEC? Some AHJ's require it, some don't care and some won't accept it because they're saying it creates a parallel pathway for a ground fault (which kinda makes sense to me). Honestly, I don't think it's needed as long as the N-G are bonded in the...