I have an insteresting scenerio on a job we are about to start:
On an existing property, a new warehouse is being built. It will be supplied by an underground 5-wire feeder from the main building, delta 3 phase, 120/240 Volts. We will keep the EGC separated from the neutral, since there will be phone and computer lines connected between the buildings, and we want to eliminate the possibility of parallel paths of returning current flow.
The main service panel enclosure will be bolted directly to "building steel"
So, the underlying question is:
Will we have to install a grounding electrode conductor from the enclosure of the panel to the building steel? If so, why? The panel is already solidly bolted to the steel ...
On an existing property, a new warehouse is being built. It will be supplied by an underground 5-wire feeder from the main building, delta 3 phase, 120/240 Volts. We will keep the EGC separated from the neutral, since there will be phone and computer lines connected between the buildings, and we want to eliminate the possibility of parallel paths of returning current flow.