MasterTheNEC
CEO and President of Electrical Code Academy, Inc.
- McKinney, Texas
- CEO
Well those would be hard pressed to meet the requirement to connect the GEC to the grounded conductor per:Typically, I just buy a few of these lay in lugs, run typically a #4 Cu conductor from water main all the way to first panel and in/out of each panel. 2 parts, quick and easy. Now, it's against code all of a sudden (or is it ? )
I'd love to get to the bottom of this. I'd rather go back to my method for last 30 years.
250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
Not sure how that would work with that lug, the method I am saying is unorthodox but compliant takes the unbroken GEC to each bus where the MBJ and grounded conductor are located, exactly as shown in the image I posted from 2014 Handbook by McPartland and Hartwell....nothing else.