Evenin' folks,
Here's a simple question for y'all....
Suppose there is a GEC run to a ground rod, which then continues to a second ground rod(required because of that pesky <25ohm rule). Is that GEC still not required to be larger than 6AWG? Or does that exception only apply if the GEC only goes to a SINGLE ground rod?
For my example, lets' use a 200A service, with no other available GE's
thanks,
Charles