chevyx92
Senior Member
- Location
- VA BCH, VA
I usually make the bonding jumper inside my XFMR and not at the first disconnecting means. I have a situation where I have parallel secondaries and just didn't see a clean way of making the bond with the parallels. Anyhow, I will have my GEC(structural steel) to my grounded conductor at my first disconnecting means. My question is, do I still need a GEC to the XFMR to bond the metal? I say no. Unless of course I overlooked something. BTW I do have EGC in all conduits to the XFMR which are landed in mechanical lugs to the frame(with paint scraped) of course.