I have an outbuilding with multiple metal water pipe underground entrances, basically at every plumbing fixture. For convenience we took the properly sized GEC to a nearby valve pit just outside the building. The inspector says that is a violation (250.52 (A) (1)) and a GEC needs to be run to an accessible connection INSIDE the building, within 5 ft of pipe entry.
Your opinion? If seems to me that the Code says the underground piping is the electrode and may be used for connection underground or inside the building within 5ft of entrance.