BLK

Member
Good afternoon - There is a facility that has a meter pedestal installed by the utility company. The pedestal is 400 amp with two 200 amp circuit breakers. Each circuit breaker is feeding a 200 amp panel. According to the utility they have bonded at the transformer. The panels then would be sub-panels with neutrals and grounds separated. Both panels are on the same building. One panel will serve a specific need while the other does the same. The question is: Does each panel require two ground rods or can they be tied together with one set of ground rods and a GEC? The other question was the size GEC? I stated, if copper, it only needs to be a #6. Please review and let me know. Thank you.

BLK
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Since it is the same building, they have to have their grounding electrode systems connected to each other. So yes, they can share ground rods. And #6 is all you need.

However, how are you getting past 225.30 (no more than one feeder to a building)?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Since it is the same building, they have to have their grounding electrode systems connected to each other. So yes, they can share ground rods. And #6 is all you need.

However, how are you getting past 225.30 (no more than one feeder to a building)?

same thoughts here
 