Leigh Simpson
The water pipe to the single family dwelling is plastic. All interior piping is PEX. Based on Table 250.66 of the 2020 NEC where do I bond and what size to a 400 amp service? There is gas piping to the house.
Table 250.66 would tell us to run a 1/0 copper to the water pipe, but this makes no sense because there is no conductive material. Also, bonding the hot - cold at the water heater makes no sense. But would you bond to the gas piping? I am confused?Article 250 Grounding and Bonding Sticky
This is a nice reference: https://www.inw-training.com/site/images/Documents/Grounding%20&%20Bonding%20Mind%20Map.pdf I'm thinking Mike Could make something like this and have it posted here as a reference sticky.forums.mikeholt.com
Are you an electrician? How to properly ground and bond a typical service should be pretty obvious.Table 250.66 would tell us to run a 1/0 copper to the water pipe, but this makes no sense because there is no conductive material. Also, bonding the hot - cold at the water heater makes no sense. But would you bond to the gas piping? I am confused?
Yes, to your question. I am not speaking about grounding, but bonding the water. If it is obvious, where would you land your 1/0? Normally, the gas is bonded/grounded at the water heater, but this cannot be done in this situation because of the PEX piping.Are you an electrician? How to properly ground and bond a typical service should be pretty obvious.
Yes, you are clear even without coffee.You bond to bring everything to equal potential. If something is non conducive there is no chance for it to become energized, so there is no point to bond it.
Hope I said that right just woke up
I agree with you, so that if the inspector insists and wants to see an outside bonding wire on the gas pipe it will be a #14 ground wire, since the furnace is on a 15 amp circuit.The EGC on your equipment that the gas is feeding would take care of that
Not required by the NEC, is this a local code amendment? If there is some types of CSST that may require an external bonding conductor.I agree with you, so that if the inspector insists and wants to see an outside bonding wire on the gas pipe it will be a #14 ground wire, since the furnace is on a 15 amp circuit.
what your proposing is accomplished at the equipmentI agree with you, so that if the inspector insists and wants to see an outside bonding wire on the gas pipe it will be a #14 ground wire, since the furnace is on a 15 amp circuit.
. . . even with a flexible gas connector? Would this compromise the bonding resistance?The EGC on your equipment that the gas is feeding would take care of that
. . . even with a flexible gas connector? Would this compromise the bonding resistance?Per International Fuel Gas Code (IFGC) 310.1 and 310.1.1 basically states if gas piping other than CSST is electrically continuous and connected to an appliance that contains an EGC then additional bonding is not required. Now CSST must be bonded at its manifold with a minimum #6 cu or #4 al bonding conductor. The above is also, referenced in the IRC as well.
There is no local amendment. Does the flexible gas connector create enough resistance that the bond is compromised?Not required by the NEC, is this a local code amendment? If there is some types of CSST that may require an external bonding conductor.
According to the American Gas Association (AGA) if the bonding mentioned above is all met then the up to 6’ of Flexible Appliance Connector (FAC) is acceptable to maintain the continuity.. . . even with a flexible gas connector? Would this compromise the bonding resistance?
Great . . . thanks for the precise answer. So much to learn. Thanks again.According to the American Gas Association (AGA) if the bonding mentioned above is all met then the up to 6’ of Flexible Appliance Connector (FAC) is acceptable to maintain the continuity.