Isn't the pipe only to be supplemented by one rod?A single ground rod is only considered a grounding electrode when it has been tested to prove 25Ω or less. If you are not testing the single rod then two rods are required.
No it needs to be supplemented by another electrode. A single rod unless tested and proven to be 25 ohms or less is not an electrode.Isn't the pipe only to be supplemented by one rod?
That's not the way I'm reading it. It says if the pipe, rod, or plate meets the 25 ohm, then no additional electrode needed. So if the pipe didn't meet it, then a rod added would satisfy that. It doesn't say a single rod is not an electrode.No it needs to be supplemented by another electrode. A single rod unless tested and proven to be 25 ohms or less is not an electrode.
250.53(2) Exception
I think you’re right250.53(D)(2) states:
If the supplemental electrode is of the rod, pipe, or plate type, it shall comply with 250.53(A).
which, when you look at 250.53(A), to me, indicates you need the two rods unless you meet the 25 ohm rule.
Sorry about that I gave the wrong code reference but the answer is the same being the bold is incorrect unless the single rod is tested. Augie gave the correct code reference.That's not the way I'm reading it. It says if the pipe, rod, or plate meets the 25 ohm, then no additional electrode needed. So if the pipe didn't meet it, then a rod added would satisfy that. It doesn't say a single rod is not an electrode.
One pipe + one rod = satisfied
You're supplementing the pipe because a single pipe, if not tested, doesn't meet the 25 ohm. The rod is the supplement. It would be the same way if it was a rod and needed supplementing, the pipe would satisfy that.250.53(D)(2) states:
If the supplemental electrode is of the rod, pipe, or plate type, it shall comply with 250.53(A).
which, when you look at 250.53(A), to me, indicates you need the two rods unless you meet the 25 ohm rule.
Note the water pipe doesn't have an allowance for checking that the resistance to ground is 25 ohms or less. The water pipe always needs a supplemental electrode. 250.53(D)(2).You're supplementing the pipe because a single pipe, if not tested, doesn't meet the 25 ohm.
250.53(A)(2) specifies that the supplement to a ground rod be an electrode "of a type specified in 250.52(A)(2) through (A)(8)". That means that a water pipe, which is the type in 250.52(A)(1), may not be the supplemental electrode to a ground rod.The rod is the supplement. It would be the same way if it was a rod and needed supplementing, the pipe would satisfy that.
No such section in the 2017, 2020, or 2023 NECs.I found the answer in 250.56
You are confusing water pipe with a piece of grc used for an electrode piece of pipe.You're supplementing the pipe because a single pipe, if not tested, doesn't meet the 25 ohm. The rod is the supplement. It would be the same way if it was a rod and needed supplementing, the pipe would satisfy that.
250.53(A) is what I posted above. It (the exception) says if you only have a single rod, pipe, or plate and it does meet the 25 ohm, then no supplement electrode needed. And since the pipe was not tested it does need a supplement and the rod would be that.
No im notYou are confusing water pipe with a piece of grc used for an electrode piece of pipe.