250.6 is about objection current. i think it is apply to the load side of service switch.
it is the question I ask at #15
I’m a bit confused about the following two scenarios:
1. A tap section in the switchboard feeds a 400A service switch using one 600 MCM copper conductor per phase and neutral, along with a 1/0 copper ground conductor in a 4" conduit. The 1/0 Cu is connected to the ground bus inside the 4000A switchboard. You mention it is violation per 250.6 Objection current.
2. Similar to scenario 1, but there is no 1/0 copper grounding conductor in the 4" conduit. Instead, the 4" conduit is bonded to both the upstream switchboard and the 400A service disconnect. Both pieces of equipment have their ground, neutral, and enclosure bonded together. I think that is how it install for the equipment. if i am wrong, please let me know.
Does the bonded conduit serve the same function as the 1/0 copper grounding conductor in scenario 1?"
And 310.10(G)(1).
The question becomes how you name the grounding conductor. If you call it a 'neutral,' then it needs to be the same size as the other neutral conductors. But if it's an equipment grounding conductor (EGC), it can be a different size than the neutral.