Is table 250-122 right for the grounding to the water meter from main disconnet? Which would be #6cu for 200a?

No see 250.66.......would require a #4 reason that can carry a fault. The sole GEC is only for objectionable current as in stray lightning current....simple analogy only.
 
Is table 250-122 right for the grounding to the water meter from main disconnet? Which would be #6cu for 200a?

Is there a requirement to bond the water meter ???? :D
even with PVC piping ?:)

As I jest, I also jump on my soap box and say that don't understand why a metal water pipe which is not a grounding electrode must be bonded per 250.66 where "other metal piping" does not carry such requirement.
 
Is there a requirement to bond the water meter ???? :D
even with PVC piping ?:)

As I jest, I also jump on my soap box and say that don't understand why a metal water pipe which is not a grounding electrode must be bonded per 250.66 where "other metal piping" does not carry such requirement.
It's on the "street side". It is a being used as a grounding electrode.
 
Is there a requirement to bond the water meter ???? :D
even with PVC piping ?:)

As I jest, I also jump on my soap box and say that don't understand why a metal water pipe which is not a grounding electrode must be bonded per 250.66 where "other metal piping" does not carry such requirement.

If the water main is plastic coming in from the street or well it does not meet the requirements of 250.52 A 1, so 250. 66 would not apply. In my area ( se Mass ) all local insp. except one use 250. 122 for this situation.
 
If the water main is plastic coming in from the street or well it does not meet the requirements of 250.52 A 1, so 250. 66 would not apply. In my area ( se Mass ) all local insp. except one use 250. 122 for this situation.

agree BUT 250.104(A) uses 250.66 also
 