Are you talking about the GEC or the EGC?
EMT only has to be bonded at one end if you are only needing to ground the conduit. If you are using the conduit as a ground, or bond, you'll need to bond it at both ends.
That being said, you only need to use a grounded 'bushing' if there are concentrics on the enclosure. If there are no concentrics, then a grounded locknut will suffice.
Make sense?
Are you talking about the GEC or the EGC?
EMT only has to be bonded at one end if you are only needing to ground the conduit. If you are using the conduit as a ground, or bond, you'll need to bond it at both ends.
That being said, you only need to use a grounded 'bushing' if there are concentrics on the enclosure. If there are no concentrics, then a grounded locknut will suffice.
Make sense?
See the illustration below and the text in red.
![]()
Roger
The comment at the bottom of that photo needs some changes. The pictured raceway is electrically continuous without the additional bonding. It needs to indicate why bonding of both ends is necessary even though it is already electrically continuous.
I beg to differ with the Bold statement above. The raceway, EMT, in the illustration is NOT continuous, it does not attach to the Ground Rod or Ground clamp.
I beg to differ with the Bold statement above. The raceway, EMT, in the illustration is NOT continuous, it does not attach to the Ground Rod or Ground clamp.
I think you're missing the fact this EMT is a sleeve for the grounding electrode conductor. Take a look at 250.64(E). Bonding needs to happens at BOTH ends of the raceway.
You're correct, I missed that fact. So, why would anyone use EMT for this purpose then?
You're correct, I missed that fact. So, why would anyone use EMT for this purpose then?
The comment at the bottom of that photo needs some changes. The pictured raceway is electrically continuous without the additional bonding. It needs to indicate why bonding of both ends is necessary even though it is already electrically continuous.
I beg to differ with the Bold statement above. The raceway, EMT, in the illustration is NOT continuous, it does not attach to the Ground Rod or Ground clamp.
It says it shall be made electrically continuous. This is done thru the bonding jumper. No?
I beg to differ with the Bold statement above. The raceway, EMT, in the illustration is NOT continuous, it does not attach to the Ground Rod or Ground clamp.
Or to the single cabinet hole it enters through to the buss bar.
If you place the leads of an ohmmeter on opposite ends of a metallic raceway you are saying you will not have continiuity? The raceway is a conductor of electricity and is electrically continuous. The reasons for bonding each end have nothing to do with continuity of the raceway and everything to do with reducing heating from magnetic effects induced on the raceway.
All I'm saying is that the metal raceway in the illustration is a sleeve and not a raceway because it is not attached to the ground rod or clamp itself there for it needs to be bonded on both ends to reduce the Choke Effect.