Dnavarro

Member
Location
Florida
Occupation
Generator builder
The pic is in a format too large to be send , sorry it is not a wire welding one we use all the time 405 A open air 90 degree but only inside the equipment we built
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The pic is in a format too large to be send , sorry it is not a wire welding one we use all the time 405 A open air 90 degree but only inside the equipment we built
No matter what, you can't exceed the 75°C ampacity rating in Table 310.16 unless all of the equipment is listed and marked for use with a higher ampacity.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
No wire welding are used Roger ,will attache a pic , this wire is allowed for use inside the machine only but no wire welding , it is an stationary unit , not rental
Well hillbilly's assumption is out of the equation
 