DavidEF543
Member
- Location
- North Carolina
- Occupation
- Electrician
A friend of mine just bought a new Generac generator and automatic transfer switch from Lowe's. The listing says it is a 22kW generator and the ATS is 200A rated for whole house power. He's doing the installation himself and asked me about wiring because he has 4/0 cable but the generator only has 2/0 sized lugs. Doing the math, 22kW is really only 100A at 220V.
The NEC says that if your generator is unable to serve the whole load that it is connected to, then you're not allowed to use an ATS, right? But this was sold as a set with a 200A ATS and he's expecting it to power his whole house. This will be an optional standby generator.
What's the deal? Is this legal? If so, how should connection be made to the generator, since the 4/0 aluminum cable has already been run and connected at the ATS. Also, if he isn't allowed to use the ATS as I suspect, could he legally just not connect the control cables and use it as a manual transfer for inspection purposes?
The NEC says that if your generator is unable to serve the whole load that it is connected to, then you're not allowed to use an ATS, right? But this was sold as a set with a 200A ATS and he's expecting it to power his whole house. This will be an optional standby generator.
What's the deal? Is this legal? If so, how should connection be made to the generator, since the 4/0 aluminum cable has already been run and connected at the ATS. Also, if he isn't allowed to use the ATS as I suspect, could he legally just not connect the control cables and use it as a manual transfer for inspection purposes?