I remember a common neutral allowance for festoon lighting.
Yes, a fairly recent change to the set up. It used to be bonded for the battery charger in the Genset, Now you have to make a separate connection. Otherwise you will get a battery error code. Found out the hard way.They now have a neutral running with it?
This case the neutral is either run a second from the ATS off the neutral bus there or jumper in the genset on the neutral bus there.Only issue in neutral jumper would be if not in the same cable, raceway, etc...which is how most older generators were wired.
300.3(B)
and also 200.4(A) prohibition of shared neutrals
Yes, a fairly recent change to the set up. It used to be bonded for the battery charger in the Genset, Now you have to make a separate connection. Otherwise you will get a battery error code. Found out the hard way.
Old configuration
View attachment 2573456
New configuration
View attachment 2573458
Have to make a jumper between J neutral and #4 NEU if you have the older ATS and older Gen cable. Prior version the neutral for the battery charger was wired internally.
Just did a liquid-cooled Generac, and the generator had the new T0 terminal. ATS didnt though.
If you have 6-control wire cable and a new ATS AND the new genset that has the 7th wire terminal (00 isolated neutral for the battery charger) can you make it work with a jumper from the primary neutral?
Do you install a neutral jumper at the generator end AND at the ATS?
Adding a 7th conductor for this installation would be a nightmare at this point.
That is the instruction from the Generac engineer.I would run a jumper at the generator and be done with it. No need to run a jumper at the ATS, the neutral on the SACM goes right back to the main neutral bar anyway.
Long enough you didn't need to activate it before it would work? They now have wifi and you must connect to internet to activate them, at least last couple I was involved with did. Kind of a pain if in location with no internet, last one I think I used my phone as an access point to do this, but someday will probably be in a place with no cell service. Might be a way to manually enter some code but haven't gone down that road yet.
It seems like usually I can't get their controller to connect to the customer wifi for whatever reason anyway.They prefer you use the wifi method, but you can still activate by phone. They want you to connect to customers wifi to get them using the Generac app. I very rarely used the wifi activation.
I installed a new 24kw at my parents house today and this is exactly what I did. I don’t remember the last Generac I installed having that separate neutral for the charging circuit.I would run a jumper at the generator and be done with it. No need to run a jumper at the ATS, the neutral on the SACM goes right back to the main neutral bar anyway.
It seems like usually I can't get their controller to connect to the customer wifi for whatever reason anyway.
Take a look at the 7163.No Generac is listed for use off grid. You should be installing the Kohler 14. It is a true off grid generator.