Generac T1 & T0 new extra wire.

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
common neutral in feeders is still in 215.4, just for some reason a branch circuit or class 1 control circuit cant share with the feeder neutral.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Edit scratch all that, since the code is permissive there would need to be a prohibition of sharing neutrals.
 

GarwoodV6

Member
Location
Houston suburbs
Occupation
30 year commercial Electrician
If you only have 6 control wires, can you still make it work by tagging the feeder neutral on the generator end? what about the ATS end?
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
They now have a neutral running with it?
Yes, a fairly recent change to the set up. It used to be bonded for the battery charger in the Genset, Now you have to make a separate connection. Otherwise you will get a battery error code. Found out the hard way.
Old configuration
1726596540339.png
New configuration
1726596797205.png
Have to make a jumper between J neutral and #4 NEU if you have the older ATS and older Gen cable. Prior version the neutral for the battery charger was wired internally.
 

shortcircuit2

Senior Member
Location
South of Bawstin
Only issue in neutral jumper would be if not in the same cable, raceway, etc...which is how most older generators were wired.
300.3(B)
and also 200.4(A) prohibition of shared neutrals
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Only issue in neutral jumper would be if not in the same cable, raceway, etc...which is how most older generators were wired.
300.3(B)
and also 200.4(A) prohibition of shared neutrals
This case the neutral is either run a second from the ATS off the neutral bus there or jumper in the genset on the neutral bus there.
New ATS diagram with a 00-NEU terminal:

1726658301122.png
Older ATS did not have this termination. Generac is still shipping (new) old stock that does not have the 00 NEU. If you get one of these the charger has to get a neutral to operate and mfg direction is to tap the J Neutral of the Genset to 00 NEU. Not to be confused with the J block of N1, N2.
To address the neutral being in same cable or raceway; the neutral being tapped IS in the same cable or raceway as it is the D neutral of the ATS 120/240 feed and would simply be a shared neutral of a MWBC. And old Genset would have this tap factory done internal to the genset.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Yes, a fairly recent change to the set up. It used to be bonded for the battery charger in the Genset, Now you have to make a separate connection. Otherwise you will get a battery error code. Found out the hard way.
Old configuration
View attachment 2573456
New configuration
View attachment 2573458
Have to make a jumper between J neutral and #4 NEU if you have the older ATS and older Gen cable. Prior version the neutral for the battery charger was wired internally.

Just did a liquid-cooled Generac, and the generator had the new T0 terminal. ATS didnt though.
 

GarwoodV6

Member
Location
Houston suburbs
Occupation
30 year commercial Electrician
If you have 6-control wire cable and a new ATS AND the new genset that has the 7th wire terminal (00 isolated neutral for the battery charger) can you make it work with a jumper from the primary neutral?
Do you install a neutral jumper at the generator end AND at the ATS?

Adding a 7th conductor for this installation would be a nightmare at this point.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
If you have 6-control wire cable and a new ATS AND the new genset that has the 7th wire terminal (00 isolated neutral for the battery charger) can you make it work with a jumper from the primary neutral?
Do you install a neutral jumper at the generator end AND at the ATS?

Adding a 7th conductor for this installation would be a nightmare at this point.

I would run a jumper at the generator and be done with it. No need to run a jumper at the ATS, the neutral on the SACM goes right back to the main neutral bar anyway.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Long enough you didn't need to activate it before it would work? They now have wifi and you must connect to internet to activate them, at least last couple I was involved with did. Kind of a pain if in location with no internet, last one I think I used my phone as an access point to do this, but someday will probably be in a place with no cell service. Might be a way to manually enter some code but haven't gone down that road yet.

They prefer you use the wifi method, but you can still activate by phone. They want you to connect to customers wifi to get them using the Generac app. I very rarely used the wifi activation.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I would run a jumper at the generator and be done with it. No need to run a jumper at the ATS, the neutral on the SACM goes right back to the main neutral bar anyway.
I installed a new 24kw at my parents house today and this is exactly what I did. I don’t remember the last Generac I installed having that separate neutral for the charging circuit.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
It seems like usually I can't get their controller to connect to the customer wifi for whatever reason anyway.

I’ve never had good luck getting them on the WiFi either. Most people just have a wireless router in the middle of the house and getting good signal outside can be difficult.
 