General Electric Gas-Filled Dry Transformers

Status
Not open for further replies.

salm10

Member
Hi all,

Can anyone shed some light on G.E.'s gas-filled dry transformers from the mid to late 1950's? I have a client who has a pair of 1000 kVA units and one of them is testing marginal with a Doble power factor test. I have worked in and around these transformers for the past 26 years and they have never had a problem. They are quite noisy, and they run hotter than heck even at half load, but they have always seemed to do the job. Unfortunately this is the first test they have ever had so there is no history to compare these results. I am skeptical of taking Doble tests at face value without corroborating bad data from other standard transformer tests. Of course, the other tests for this unit (midroohmmeter, megohmmeter, polarization, dielectric absorption, ttr, etc.) are all ok.

Considering just their age I am recommending replacement, but my customer would like to know if there are people in the industry who know more about them.

Many thanks, always.

PS. Forgot to mention, 4160 volt primary, 208/120 secondary
 
I know the units you are talking about, I have tested a few and they have always been OK, so cant help you on Pf results, what did you get for %Pf?
 
The PF came in at 18.18% with high side energized and low side guarded. Doble is calling this reading a D deteriorated. The other two Doble readings were 5.53% and 0.513%
 
Yikes, the limit on that unit is 3%.

Did you do the whole test #1-Test #2 and compare to UST thing to verify your results?
 