wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Not following you--if it has 10 fixtures on it, that's 10 separate loads, and you'd determine separately for each load whether it is continuous or not.If the lighting circuit had 10 fixtures connected to it but only 9 fixtures were on at one time for more than 3 hours that would not be considered a continuous load. The max load would be when all connected fixtures were on at one time.
Cheers, Wayne