Generater Back Up

Status
Not open for further replies.

jute

Senior Member
Location
SO CAL
I have an apt building that consist of 20 apts. It has (2) buildings with (10)apts on each side. They had a power outage for 13 hours and now want a back up system for the exterior lighting, power for the gates and power in the office in the event that this happens again. I haven't done this before and would like suggestions on what I should offer therm. I imagine I would take a load calc of what they want on the back up system to know what size generater and then install a seperate panel for the loads and generater to control. I'm not sure how this would be set up and how the tranfer switch would work, Where can I find info on how to set this up and if a generater is the best application for this? Thanks, JB:-?
 
You could probably use the feeder for the house panel to feed the ATS and then the load side of the ATS to feed the house panel.
 
Thanks for the reply... I understand the concept of this but do not know how to set this up. Where would I find info on how to set this up correctly? Thanks, JB
 