donw:
You are listed as an engineer. What kind?
If you are an electrical engineer, then I would not expect your questions as presented.
It seems you have stove store with a 3 phase delta secondary 240 V line to line and the secondary is corner grounded. This secondary has nothing that could be called a neutral.
What kind of a stove store would have use for this type secondary and grounding?
I don't believe you have indicated whether or not you require an AC supply with a center tapped 240 V secondary (this sort of implies that this secondary is electrically isolated from anything else until you choose to connect it to something), or simply need 120 V.
I am sort of implying from your comments that you only need 120 V, but this is not clear. In this case the secondary could be grounded or not grounded, but if one line was grounded that would not be a neutral.
You have not indicated the power capability of your 3 phase delta, but I assume it is moderately large.
You have not indicated what your 120 V load is, but I assume small compared to the 3 phase transformer.
In any event you need an isolation transformer from 240 to 120 or 240 center tapped that can handle your 120 V load. No need to change the corner grounding of the 3 phase secondary. Your 120 secondary gets grounded as needed.
Looking at the title of the thread --- if you could remove the corner grounding without causing some sort of problem for what the store requires, and replace one 240 secondary with a center tapped winding, then you probably could ground that center tap. The wire to the center tap could now be called a neutral relative to 120 V loads on both sides of the center tap. Grounding of the center tap does not define whether to call the wire a neutral or not, but usage of the two 120 windings is the determining factor.
.