So reactance number has nothing to do with short circuit calculation.Because you tell it when you enter the Bus base kV!
Case 1: 250KVA 208V generator, 250KVA alternator, 480V base, X0=A, X'=B, X"=C.
Case 2: 250KVA 208V generator, 250KVA alternator, 208V base, X0=D, X'=E, X"=F.
So when I input these two case, I will get same result, because my bus base KV is 208.
It does not make sense to me, because these two case has different X0, X', X"