I am working on a bank operations center that will have the whole building (less electric zone strip heats to suppliment gas heat). 150KW generator so capacity is not an issue.
Building has lots of computers, each with it's own UPS for carry-over during the transfer time.
The generator will start within 10 seconds.
Can I omit the battery backed-up emergency and exit lights?
Do I have to have a dedicated transfer switch for "life safety," or is that requirement only for a hospital?
Thanks
RC
Building has lots of computers, each with it's own UPS for carry-over during the transfer time.
The generator will start within 10 seconds.
Can I omit the battery backed-up emergency and exit lights?
Do I have to have a dedicated transfer switch for "life safety," or is that requirement only for a hospital?
Thanks