Generator and multiple buildings

Status
Not open for further replies.

badgers

Member
To setup my question please look at the attached sketch.

Is it allowed to even bring the life safety circuits to the new building?

if so, should I bring 4W + gnd and then bond the gnd with the building steel?

Any suggestions or comments on this would be appreciated.

thank you
 
Is it possible to inline the image?
attachment.php
 
sorry about the image problem, It just seemed that a picture would make it easier to understand the situation.
 
This is another interesting question. It is similar to the question posted here:

http://www.mikeholt.com/code_forum/showthread.php?t=79292

But this question differs from the other question in one key way. In this case, the second power supply is for an emergency circuit. You will note that both 225 and 230 include emergency circuits in the list of acceptable reasons for having two feeders or for having two services.

The two questions are similar in this way: In one case, we are looking at one service and one branch circuit. In the other case, we are looking at one service and one feeder. So in neither case does 225 have the answer, and in neither case does 230 have the answer.

If I can find my list of issues that were possible submittals for the 2011 NEC, I?ll add this one to the list.
 
My first reaction is that the ground from the new building is tied to the second building. They are from seperate utility transformers.
The voltage drop on the neutral in from the old building won't be the same as the voltage drop on the new building.

I was of the opinion to set a transformer at the new building and derive a new neutral and ground for the new building.
thanks
 
badgers,

Let's say bld. #2 the main power is lost, bld. #1 is still good with their

power, bld #2 will not receive EM power and that's no good.
 
Charlie:

In my opinion, this is allowed, and I think it s done all the time. Don't you agree that if the NEC doesn't prohibit it, then it is allowed? (I think I might have even learned that from you:D )

However, I am concerned when the original question says "Building B wants a life safety circuit". Life safety circuits are required. The only equipment you can put on a life safety circuit are loads that are legally required. If they just have some lights in building B that they would like to run during a power outage, thats a whole new ballgame.

Steve
 
benaround said:
badgers,

Let's say bld. #2 the main power is lost, bld. #1 is still good with their

power, bld #2 will not receive EM power and that's no good.


That won't happen because the emergency feeder to building #2 will still have normal power supplying it from building #1. No need to run extra wiring for start contacts.

Steve
 
benaround said:
steve66,

That's a good point!!!!!


No problem, but I know what you're thinking of. That can easily happen with the frog eye battery lights if they aren't on the right circuit!!

Steve
 