Acxpert
Member
- Location
- San Francisco, CA USA
With the pending PG&E outages looming I am looking at installing an 11kW Generac generator and transfer switch. My main panel is a 200 amp combo service entry with meter and load center.
Looking at the transfer switch literature it says to "disconnect bonding connection in panelboard". Problem is that my panel doesnt have separate neutral and grounding bars and everything is tied together. It would be a nightmare if not impossible to separate them and even it I found a way I would have to make a bunch of splices.
So, would it be acceptable to run separate ground and neutral wires from the generator and connect them to the common neutral/grounding bar in the load panel?
Looking at the transfer switch literature it says to "disconnect bonding connection in panelboard". Problem is that my panel doesnt have separate neutral and grounding bars and everything is tied together. It would be a nightmare if not impossible to separate them and even it I found a way I would have to make a bunch of splices.
So, would it be acceptable to run separate ground and neutral wires from the generator and connect them to the common neutral/grounding bar in the load panel?