I have a new building with the incoming voltage from the utility at 208V. This is a very small new building and will be part of an existing building complex with other buildings fed from 480V. The complex is also backed up from a 480Y/277V standby/emergency power generator.
For emergency/standby power for this new small building, since the utility and generator voltages do not match, am I allowed to provide a transformer ahead of the building ATS' so I can derive 208V from the generator and provide 208V from the utility? Or do I have to tell the utility to provide a 480V transformer for the building to match the generator?
Looking in the NEC, I do not see anything that specifically tells me that the generator voltage must match the utility voltage. However, Article 705.14 Output Characteristics states, "The output of a generator or other power production source operating in parallel with an electric supply system shall be compatible with the voltage, wave shape, and frequency of the system to which it is connected." Also, a FPN states, "The term compatible does not necessarily mean matching the primary source wave shape."
Do I make the utility and generator voltages COMPATIBLE by utilitizing the transformer on the primary side of the ATS?
Thanks,
Mike
For emergency/standby power for this new small building, since the utility and generator voltages do not match, am I allowed to provide a transformer ahead of the building ATS' so I can derive 208V from the generator and provide 208V from the utility? Or do I have to tell the utility to provide a 480V transformer for the building to match the generator?
Looking in the NEC, I do not see anything that specifically tells me that the generator voltage must match the utility voltage. However, Article 705.14 Output Characteristics states, "The output of a generator or other power production source operating in parallel with an electric supply system shall be compatible with the voltage, wave shape, and frequency of the system to which it is connected." Also, a FPN states, "The term compatible does not necessarily mean matching the primary source wave shape."
Do I make the utility and generator voltages COMPATIBLE by utilitizing the transformer on the primary side of the ATS?
Thanks,
Mike
Last edited: