Is there any code requirement for: quantity and specific location of emergency generator annunciator panel and its EPO? Thanks!
 
Genset Annunciator Location

Genset Annunciator Location

A lot is dependant on your system. Is this a "Legally Required Standby System"? NFPA 110-Standard for Emergency and Standby Power Systems, requires that Remote Controls and Alarms be "...located outside the EPS service room at a work site readily observable by personnel." NFPA 110,3-5.6.1. There are other provisions as well. Some AHJ's require the location be a "constantly attended location". And there are VERY specific requirements as to what must be monitored, (Table 3-5.5.2(d)-Safety Indications and Shutdowns).