Generator as a separately derived system

No, it is not code compliant to disconnect. I can't imagine that you can't disconnect the bond between the neutral to the ground in the generator, though.
 
So, to avoid code violation, can the EGC between the Generator and the Disconnect be disconnected?
The NEC has very limited allowances for using other than a dedicated bonding/grounding conductor for ground fault clearing. There's the allowance to use the grounded service conductor on the supply side of a service disconnect, as well as an allowance for circuits originating at an outdoor transformer. I don't believe there is any allowance for a generator.

So no, you need to install an EGC/bonding jumper between the generator and the disconnect. Your solutions to avoiding multiple N-G bonds in the system are only to remove the N-G bond at the generator, or use an ATS that switches the neutral. That's it.

Cheers, Wayne
 
I can't imagine that you can't disconnect the bond between the neutral to the ground in the generator, though.
These portable units they sell at all the big box stores, is there a jumper or a screw to lift the neutral ground bond? The only times I've worked on them was for applications that needed a n-g bond so I never paid any attention

I'm willing to bet most of them are hooked up to building wiring with the N-G bond intact just due to ignorance
 
Okay going back to this....

... I understand using a neutral switching transfer switch definitely makes a neutral bonded generator a SDS. However, to avoid the double N-G bonds issues, I am being told by a company that I should use a non-neutral switching transfer switch with the neutral bonded generator but don't connect the ground to the transfer switch. It doesn't sound quite right so I am doing a sanity check.

The 'company' seems to be wrong. This describes two incompatible methods.

Either...

1: SDS setup:
Neutral is switched
N-G bonds at service *and* generator

OR

2: Non-SDS setup:
Neutral is not switched
N-G bond required at service, prohibited anywhere else (including generator)

If you have a generator with an N-G bond that cannot be removed, then 1 is the only option. If you have a transfer switch that doesn't switch the neutral, then 2 is the only option. You can't use these two pieces of equipment in the same system.
 