Here are the facts:
Objective is to replace the manual transfer switch with an automatic one.
Normal power at service is 480/277v at 200a 3ph fused at 200amp in 3R disconnect immediately at where the existing service entrance rated manual transfer switch is located just on the inside. Txfer switch is fused on both normal and alternate power at 200amps. All conductors on and in the building service equipment are 3/0 cu.
Alternate power is 140kw 480/277v with @214amp output with a 250amp internal breaker. A 4/0 W type cable feeds from the gen. to a pin & sleeve 200amp receptacle on the exterior of the building immediate to where the service rated manual txfer switch is on the inside.
I have asked about changing the gen breaker to 225amp rating and it is not UL designed for the 225amp I am told.
Can I upgrade the conductor on the load side of the Pin and sleeve receptacle to 4/0 cu thhn and on through a non service entrance rated AUTOMATIC Txfer switch to the main switchboard, and meet code?
My thinking is that I have to have an OCPD (fused disconnect) on exterior, but then I cannot incorporate the receptacle into the system, which may be ok and will probably wind up doing anyway.
Thanks for any and all input,
MD
Objective is to replace the manual transfer switch with an automatic one.
Normal power at service is 480/277v at 200a 3ph fused at 200amp in 3R disconnect immediately at where the existing service entrance rated manual transfer switch is located just on the inside. Txfer switch is fused on both normal and alternate power at 200amps. All conductors on and in the building service equipment are 3/0 cu.
Alternate power is 140kw 480/277v with @214amp output with a 250amp internal breaker. A 4/0 W type cable feeds from the gen. to a pin & sleeve 200amp receptacle on the exterior of the building immediate to where the service rated manual txfer switch is on the inside.
I have asked about changing the gen breaker to 225amp rating and it is not UL designed for the 225amp I am told.
Can I upgrade the conductor on the load side of the Pin and sleeve receptacle to 4/0 cu thhn and on through a non service entrance rated AUTOMATIC Txfer switch to the main switchboard, and meet code?
My thinking is that I have to have an OCPD (fused disconnect) on exterior, but then I cannot incorporate the receptacle into the system, which may be ok and will probably wind up doing anyway.
Thanks for any and all input,
MD