mkgrady
- Massachusetts
I have been doing a fair amount of home standby generator installs lately but I'm not sure how to do this one. Normally I will calculate the size generator required, put in a smart service rated ATS to control AC systems and use contactors to control heavy loads like ovens and dryers. In every case I wind up putting in a 10-20KW generator and either a 100 or 200 amp ATS.
On this job the service is rated 300 amp. probably because he has so many big woodworking power tools. If it were not for that a 200 amp service would have been the right size and most likely a 20KW generator would have been the right size. I'm thinking I could put the wood shop on a contactor that would be controlled by the smart ATS
The 300 amp service meter feeds a 200 amp panel that feeds most of the house and the meter also feeds a 100 amp panel that feeds a smaller portion of the house but the part they use the most. So both panels must be powered by the generator.
I'm trying to figure out what the ATS should be. I don't think a 300 amp ATS is made. Is my only choice to use a 400 amp service rated ATS and use the smart features to limit the load on the generator? I'm thinking yes but hoping for other suggestions because I imagine a 400 ATS is very large and space is limited.