EEC said:The generator is an emergency source that is tapped into two 400 amp service rated disconnects. Then from there too two ATS, one for elevator 3 phase solid nuetral ATS and the other 4 pole switched neutral ATS for building emergency loads, ie lighting etc.
Whats wrong with bonding at the two disconnects and not at generator?
And
RUWired said:In the situation with (1) switched neutral and (1) solid neutral, The only bonding taking place will be at the main service. The ground and neutral are seperated even at the (2) generator disconnects. Otherwise you'll have parallel paths on the ground wire with the solid neutral feeder. The fault current path with the switched neutral will flow back to the main service bond and then continue back to the generator via the neutral of the solid neutral feeder and trip the generator breaker on that feeder of the fault.
Rick
EEC, Aside from the generator source are the ATS?s ?served? (utility) or ?fed? (premises distribution)?