Generator breaker sizing

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
I have emergency generator 200kva, 480V, 3 phase. What would be appropriate overcurrent size for the emergency generator per Nec 2014?

Sent from my SM-G935U using Tapatalk
 
I have emergency generator 200kva, 480V, 3 phase. What would be appropriate overcurrent breaker size (OCPD) for the emergency generator per Nec 2014?



Sent from my SM-G935U using Tapatalk
 
Yea but in my case I have to update the emergency generator load and so I was wondering what the new circuit breaker size be. I have 225 amps ATS downstream.

Sent from my SM-G935U using Tapatalk

Then there's your answer, 225 amps. Just make sure there's less than 225 amps of load at any given time.
 
Their was change order. Ats is now 250 amps. So FLA is less than 250 amps. How does this work in terms of sizing breaker?

Sent from my SM-G935U using Tapatalk

When you get all the changes in order come back and start a new thread with all the correct information.

Roger
 