Generator Cables

Merry Christmas
Status
Not open for further replies.
Re: Generator Cables

most of the time you fine this conductors inide the units and this unit is UL listed so dont worry obout
 
Re: Generator Cables

Lawelectric:

Wow you are almost as smart as me. You learn from your mistakes. (454,975) If that is over a ten year span you'll catch me in another 40 or 50 years. :D :D
 
Re: Generator Cables

Originally posted by wilsa:
most of the time you fine this conductors inide the units and this unit is UL listed so don't worry obout
Regardless of what is inside the unit we as professionals still have to follow the NEC don't you think?
 
Re: Generator Cables

The cables being discussed are the "hook up cables" between the load side of the generator output breaker and premise wiring of the building that requires temporary power; not the internal, factory wiring of the mobile, or portable generator.
 