sparkyjpb Member Location S/E Michigan Apr 22, 2011 #1 For residential standby generator conductors, do I size do them using 310-16 or 310-15 (B) (6)?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 22, 2011 #2 From the wording, I see no problem with your using 310.15(B)(6) as long as the feeder serves the entire load of the dwelling unit.
From the wording, I see no problem with your using 310.15(B)(6) as long as the feeder serves the entire load of the dwelling unit.