ptonsparky
Tom
- Occupation
- EC - retired
I have ordred tray cable in the past. DB and sunlight resistant. Limited to where you can use it and you will have to determine the class 2 problem.
They are using n1 n2 as the utility sensing and the other is T1 it is the ungrounded wire for the batt. charger you pick up the neutral in the generator to complete the circuit
Most of Generac's instructions state if you go over the 30ft factory whip or do not use it then they must be separated. As long as the insulation rating is over the voltage being produced then they can go in the same conduit. I know that you must follow the Mfg's instructions but there is no real reason the wiring must be separated. The control wires are running 240v utility voltage. If utility drops out a set of contacts close and the gen. starts. The ATS and gen are not "talking" to each other so EMFs wouldn't bother any thing.
FWIW, I thought all wiring inside the Xfer switch cabinet had to have the same insulation rating, irrespective of the voltages. That's why I don't run the 18/2 t-stat AC condenser activation wiring into the Nexus load management system. I usually install a 4 x 4 x 2 PVC JB under the cabinet and chase nipple it in. I then splice on # 14 THHN's to the 18/2 and run that into the NexusI use and only because it is what is specked. 18 ga stranded, 8pr, individually shielded, direct bury cable. I do not run 240 volts in it but I think it is rated for 300v like SJ cord. Our price is something like $1.20 per ft if I buy it in 1000ft spools.
Welcome to the world of Generac. Try this company :As you can tell I'm not fond of Generac after they went to dealer for parts, they wont even allow you to talk to their tech deparment if you have a question, I cant even get a tune up kit or filters unless I'm a dealer or a tech for them, and to become one they want you to stock a whole bunch of parts you may never use, sorry don't have that kind of money, so now if a customer buy's one I'll install it, but I spell it out service or repairs to be done by others.
As you can tell I'm not fond of Generac after they went to dealer for parts, they wont even allow you to talk to their tech department if you have a question, I cant even get a tune up kit or filters unless I'm a dealer or a tech for them, and to become one they want you to stock a whole bunch of parts you may never use, sorry don't have that kind of money, so now if a customer buys one I'll install it, but I spell it out service or repairs to be done by others.