445.18A Requires a lockable disconnect on a generator. What is it for? What would it do that the breaker in the generator doesn't do?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
I think that the breaker qualifies that is under the generator cover, cause those covers are lockable.
 

Danielt

Member
Location
VIRGINIA
Occupation
Master Electrician
But if the disconnect is on the conductors going to the transfer switch, they aren't energized unless the generator is running, so why disconnect them while servicing?
If you're servicing the generator and need to run it, you turn off the internal breaker. Or even if you don't, you're just energizing the wires to the transfer switch, where they'll stop.
The only energized conductors in the generator are the control/monitoring wires, which are usually line voltage. These are the only ones that seem to need a disconnect, but that's not what 445.18 seems to be saying
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is this what it says a “lockable breaker” or a “lockable disconnect” if the latter, any means of disconnect under a lockable cover should qualify
A lock on a cover never equals a locked device...a disconnect lock must lock the breaker or switch operating handle.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Are you talking about a disconnect at a building for a generator that is located remotely from the building?

If so, that's no different from a disconnect for any separate structure. The genny is a remote power source.

I haven't installed a disconnect at a generator, but I've used a non-fused AC disconnect on a house wall.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I designed a panelboard cover lock that OSHA liked, you turned off the breakers you wanted, the bar prevented the cover from being opened, and a lock and key that only the person that installed it has. Where it is not legal, is using the factory cover lock that uses a common key.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I designed a panelboard cover lock that OSHA liked, you turned off the breakers you wanted, the bar prevented the cover from being opened, and a lock and key that only the person that installed it has. Where it is not legal, is using the factory cover lock that uses a common key.
Do you have any official document from OSHA that says that is an acceptable lockout?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Then that would apply to a panel board cover with a lock in the door, the issue is the cover can be removed.
And everybody and their brother has a factory key. On a side note though, panelboards usually require the door to be open, before the cover screws can be removed. But loadcenters, yes, the cover can be removed.
 

Danielt

Member
Location
VIRGINIA
Occupation
Master Electrician
Are you talking about a disconnect at a building for a generator that is located remotely from the building?

If so, that's no different from a disconnect for any separate structure. The genny is a remote power source.

I haven't installed a disconnect at a generator, but I've used a non-fused AC disconnect on a house wall.
I'm trying to understand the code reference from the op , and my previous comment. Everyone is hung up on the locking aspect, I'm wondering about the purpose or point of having a disconnect. Does the breaker in the generator fill the need for a disconnect in 445.18?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Then that would apply to a panel board cover with a lock in the door, the issue is the cover can be removed.
Exactly,
To remove a cover that is locked is a secondary action most likely performed by a individual knowledgeable of possible hazards.
So I guess the question is, does the code specifically say the device needs locked or that a means to lock the disconnect applies?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
I'm trying to understand the code reference from the op , and my previous comment. Everyone is hung up on the locking aspect, I'm wondering about the purpose or point of having a disconnect. Does the breaker in the generator fill the need for a disconnect in 445.18?
We’re debating here about this, because some of us believe that breaker qualifies if satisfied by the language and intent of the code.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Exactly,
To remove a cover that is locked is a secondary action most likely performed by a individual knowledgeable of possible hazards.
So I guess the question is, does the code specifically say the device needs locked or that a means to lock the disconnect applies?
The code language in 110.25 says the disconnect must be lockable in the open position....the cover is not the disconnect.
 

Danielt

Member
Location
VIRGINIA
Occupation
Master Electrician
We’re debating here about this, because some of us believe that breaker qualifies if satisfied by the language and intent of the code.
Okay.
I believe when the code says lockable, it's a reference to OSHAs lockout/tagout. Neither the generator breaker nor the cover have means of locking it out, of placing a physical lock on it.
Therefore, a disconnect is called for by Code.
If it's on the conductors between the generator and the transfer switch, what is it for? To work on the transfer switch safely?
The only reason I could come up with is a fire situation, and the generator is running, and the fire department can disconnect the generator from the building. But they would fist get to the switchgear/main to disconnect normal power,as they would if the building didn't have a generator.
But then why have it lockable? As I said , that is usually a requirement for servicing equipment.
 