A lockable cover does not equal a lockable breaker.I think that the breaker qualifies that is under the generator cover, cause those covers are lockable.
Is this what it says a “lockable breaker” or a “lockable disconnect” if the latter, any means of disconnect under a lockable cover should qualifyA lockable cover does not equal a lockable breaker.
A lock on a cover never equals a locked device...a disconnect lock must lock the breaker or switch operating handle.Is this what it says a “lockable breaker” or a “lockable disconnect” if the latter, any means of disconnect under a lockable cover should qualify
It should when a device is behind that lockable cover.A lock on a cover never equals a locked device...a disconnect lock must lock the breaker or switch operating handle.
Sorry...it doesn'tIt should when a device is behind that lockable cover.
Do you have any official document from OSHA that says that is an acceptable lockout?I designed a panelboard cover lock that OSHA liked, you turned off the breakers you wanted, the bar prevented the cover from being opened, and a lock and key that only the person that installed it has. Where it is not legal, is using the factory cover lock that uses a common key.
Then that would apply to a panel board cover with a lock in the door, the issue is the cover can be removed.It should when a device is behind that lockable cover.
And everybody and their brother has a factory key. On a side note though, panelboards usually require the door to be open, before the cover screws can be removed. But loadcenters, yes, the cover can be removed.Then that would apply to a panel board cover with a lock in the door, the issue is the cover can be removed.
I'm trying to understand the code reference from the op , and my previous comment. Everyone is hung up on the locking aspect, I'm wondering about the purpose or point of having a disconnect. Does the breaker in the generator fill the need for a disconnect in 445.18?Are you talking about a disconnect at a building for a generator that is located remotely from the building?
If so, that's no different from a disconnect for any separate structure. The genny is a remote power source.
I haven't installed a disconnect at a generator, but I've used a non-fused AC disconnect on a house wall.
Exactly,Then that would apply to a panel board cover with a lock in the door, the issue is the cover can be removed.
We’re debating here about this, because some of us believe that breaker qualifies if satisfied by the language and intent of the code.I'm trying to understand the code reference from the op , and my previous comment. Everyone is hung up on the locking aspect, I'm wondering about the purpose or point of having a disconnect. Does the breaker in the generator fill the need for a disconnect in 445.18?
The code language in 110.25 says the disconnect must be lockable in the open position....the cover is not the disconnect.Exactly,
To remove a cover that is locked is a secondary action most likely performed by a individual knowledgeable of possible hazards.
So I guess the question is, does the code specifically say the device needs locked or that a means to lock the disconnect applies?
Okay.We’re debating here about this, because some of us believe that breaker qualifies if satisfied by the language and intent of the code.