I have searched and read - there was a previous thread about the generator disconnects, but I see no conclusive continuous logically trail.
700.12.B.6) Outdoor Generator Sets. Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure.
Here is the exception. What is the rule it is excepting?
I have a client who is sighing at my insisting on putting in disconnects.
I have a colleague who says it isn't a service, so he isn't putting in disconnects where the generator conductors enter the building under any circumstance.
So please supply me with a logical thread.
Also, if you use the 225.31, 225.36 argument - then service entrance rated means a jumper between the neutral and the ground in the disconnect. I definitely don't want this. Either I am not switching the neutral and there is a solid neutral which will be bonded in the MDP, or I am switching the neutral and will bond between the neutral and the ground at the generator. I would never want to bond at the disconnect. Please comment.
700.12.B.6) Outdoor Generator Sets. Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure.
Here is the exception. What is the rule it is excepting?
I have a client who is sighing at my insisting on putting in disconnects.
I have a colleague who says it isn't a service, so he isn't putting in disconnects where the generator conductors enter the building under any circumstance.
So please supply me with a logical thread.
Also, if you use the 225.31, 225.36 argument - then service entrance rated means a jumper between the neutral and the ground in the disconnect. I definitely don't want this. Either I am not switching the neutral and there is a solid neutral which will be bonded in the MDP, or I am switching the neutral and will bond between the neutral and the ground at the generator. I would never want to bond at the disconnect. Please comment.