I am working in a building with all power de-energized and the contractor needs lighting for some of the interior work to be performed.
They are asking to hook a single circuit of existing lights (eight light fixtures total) to a portable generator to provide the light they need.
There is nothing else connected to this row of lights.
They have disconnected the the branch circuit from the feeder in a junction box and have connected this single circuit to the generator. (this has already been done and functioning properly when I was asked of the legality of it).
Question is, is this legal? I have been looking through the code book and found a reference not allowing it (250.34 A 1) The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator. or both, but have not found anything allowing it.
I am thinking that since it is temporary there may be a code reference allowing it even though 590.3 (A) states: Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.
Any help would be greatly appreciated. any code references would also be appreciated.
Thank you
Thank you