I guess there aren't that many.
Since five of the main disco's six neutral terminals are in use (neutral in, neutral out, EGC out, and two GECs), and the ATS/generator's neutral uses the sixth hole, can the EGC (#8cu based on the 70a generator's feeder) either:
A. Land on a lug bolted to the main disco's enclosure?
B. Be split-bolted to one of the existing bare GEC's?
Added: So the capacity questions have to do with which loads may be left on when the ATS switches over, right, and not everything in the house a careless customer might attempt to use?