Jerseydaze
Senior Member
Do you calculate gen feeders at 100% rating of generator or 125%
from the 08
445.13 Ampacity of Conductors.
The ampacity of the conductors from the generator terminals to the first distribution device(s) containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator. It shall be permitted to size the neutral conductors in accordance with 220.61. Conductors that must carry ground-fault currents shall not be smaller than required by 250.30(A). Neutral conductors of dc generators that must carry ground-fault currents shall not be smaller than the minimum required size of the largest conductor.
Exception: Where the design and operation of the generator prevent overloading, the ampacity of the conductors shall not be less than 100 percent of the nameplate current rating of the generator.
Jerseydaze said:Do you calculate gen feeders at 100% rating of generator or 125%
Nor have I.iwire said:I have never wired a generator that did not already have an overcurrent device installed on it
I wouldn't say that. That section tells me to size my conductors as per T310.16.making that section meaningless.
chris kennedy said:I wouldn't say that. That section tells me to size my conductors as per T310.16.
chris kennedy said:Which way are we working here Bob? Sounds to me like OP has a generator already. Your sizing your feeders for the load which in turn would tell you the size of the OCP and gen-set.
Jerseydaze said:Do you calculate gen feeders at 100% rating of generator or 125%
iwire said:How do you calculate a feeder supplied from a service?
Feeders shall have an ampacity not less than the noncontinuous loads plus 125 percent of the continuous loads. 215.2(A)(1)
Jerseydaze said:I know some of you think its helpfull to chastise guys for not knowing something obvious to you.I think its beter to ask something stupid then do something stupid.
Jerseydaze said:I know some of you think its helpfull to chastise guys for not knowing something obvious to you.
Pierre C Belarge said:It will be based on the size of the overcurrent device on located at the generator., if the device at the generator is not just a disconnecting means but also is an overcurrent device.
iwire said:You felt you where chastised in this thread? :-? :-? :-? :-? :-? :-? :-?