Ran across this today.
New work in progress.
The way I see it is you need four pole ats.
There were talking changing the generator from an SDS to an optional stand by since they have unswitchd neutrals im the ats's.
Both buildings have GFI protection in the switchgear. I see this as a issue causing the GFI to trip due to the neutrals of the two systems tied together through the generator and ats's. Plus would this lead to recirculating currents issues.
Here Is a rough sketch.
I recommend they contact the engineer.
I'm I understanding it correctly.