Re: Generator grounding and bonding
If you switch the neutral, then you will treat the connection similar to a service connection.
You connect the equipment ground conductor and the grounding electrode conductor together with the gounded conductor, bonding to the enclosure.
If you do not switch the neutral, then you will treat the connection similar to a "subpanel".
You connect the equipment ground conductor and the grounding electrode conductor to the enclosure. The grounded conductor is isolated from those connections.