Re: generator grounding
Mark that is an interesting question I had not considered.
First off the generator is not a 'service'
Supplied from a Common Service
That being the case a generator out on it's own with only the feeder from the generator running into another structure would not require a grounding electrode.
However, many times there will be one or two branch circuits or a feeder running from an AC service in a separate structure to the generators location for the purposes of charging the battery and keeping the engine and sometimes the battery warm.
In that case IMO 250.32 requires a grounding electrode at this separate structure (the generator).
JMO, Bob
Mark that is an interesting question I had not considered.
I think the answer is it depends.250.32 Two or More Buildings or Structures Supplied from a Common Service.
(A) Grounding Electrode. Where two or more buildings or structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.
First off the generator is not a 'service'
Supplied from a Common Service
That being the case a generator out on it's own with only the feeder from the generator running into another structure would not require a grounding electrode.
However, many times there will be one or two branch circuits or a feeder running from an AC service in a separate structure to the generators location for the purposes of charging the battery and keeping the engine and sometimes the battery warm.
In that case IMO 250.32 requires a grounding electrode at this separate structure (the generator).
JMO, Bob