fisherelectric
- Northern Va
Customer has a 40 KW generator that's been wired for 120/240 volt operation with a 180 amp breaker. His house has 2 200 amp service disconnects in the garage with 4/0 SER feeders running to load centers in the basement. He wants to install 2 manual 200 amp transfer switches between the disconnects and the load centers. He wants to run 4/0 SER from the generator to a trough beside the transfer switches and then run 4/0 into each transfer switch. Is that compliant?
He has gas heat and cooking and water heater. Five small AC units the largest of which has MCA 22 amps.